Re: [Phys-L] new physics lab construction
- From: John Denker <jsd@av8n.com>
- Date: Sun, 28 Sep 2014 13:48:49 -0700
On 09/11/2014 07:19 PM, Larry Smith wrote:
> We are in the process of “programming” for a new science building
Here's an all-too-common story, forwarded from the
chemistry list:
On 09/28/2014 11:48 AM, ssmaglik wrote:
>> The architects of our brand new science building didn't account for the
>> ventilation of or flammables. We have put all of our liquid organics in a
>> flammables cabinet but when we open the door, we are overwhelmed with
>> noxious odors. Anything we suggest to vent the cabinet will compromised
>> the flammability suppression of the cabinet. Anyone have any suggestions
>> to vent this cabinet and/or protect its contents, while allowing us to
>> breathe easy? Oh, and without a total remodel of the room?
Some thoughts:
0) Do not underestimate the potential for screw-ups.
1) It's worth your while to get a really good architect. The
cost of the architect is small compared to the cost of construction.
It pays for itself if it prevents even one screw-up.
The situation is similar to car-repair shops: Some of them are
really good, but the other 90% of them aren't. There ought to
be a way to tell the difference before it's too late, but that's
not easy. Talking to a few previous customers helps.
2) You might want to get a second opinion, i.e. to have an independent
professional double-check the plans. There are firms that specialize
in this:
https://www.google.com/search?q=architect+%22second+opinion%22+review
3) It also pays to set up a user committee drawn from the folks
who will actually be using the building. There are books that
they can read so they can get up to speed on what features are
possible, and on what mistakes should be avoided.
Keep the committee small. One diligent review is far more valuable
than a huge number of superficial glances.
4) At a more detailed level: Anything that is lab space, or might ever
become lab space, should back up against a /service corridor/ aka
/utility core/ so that things like additional fume ventilation, gas,
water, sewer, wiring, etc. can be added without having to reconstruct
the entire building.
This has been standard practice in lab construction for 50 years that
I know of, maybe more, so it's embarrassing to even mention it. Leaving
out the utility core would count as a monumental screw-up, but such
things can happen if you're not vigilant.
5) Think about the /real/ safety issues. Nowadays some people think
that means minimizing the number of doors, so that you can protect
the place against a crazed gunman. In fact, the typical school can
expect to have a gunman problem once every several thousand years.
The chance of a fire or toxic chemical spill is far greater, which
is why you want safety showers, eye-wash stations, shutoff switches,
and /more/ doors, not fewer. Emergency exits can be locked and
alarmed, you know.
Showers and eyewash stations should always be alarmed. Rationale:
you don't want to choose between washing and going for help.
6) Speaking of alarms: Make sure you have a "general evacuation alarm"
not just a fire alarm. Rationale: Suppose there is a toxic chemical
spill. You want to get everybody out. It is next to impossible to
get the typical person to pull the "fire" alarm if there is not an
actual blazing fire. Also, you want emergency responders to know
they're dealing with a problem other than a fire. Plan for this.
Explain this to denizens ... and visitors. Drill for this.
At the door to each lab room, there should be a shutoff switch aka
panic button that shuts off the natural gas supply to the room and
all of the electricity except for special circuits for emergency
lighting, fume hood ventilation et cetera. This is one of those
things that is cheap to design in at an early stage and expensive
(albeit not impossible) to retrofit.
Amazingly enough, you can still find places that don't have any such
feature.
7) As previously mentioned: Design for flexibility!
This includes designing relatively large areas that can be broken
up with NON-load-bearing walls. That way you can rearrange walls
as needs change during the life of the building ... e.g. turning
one large room into N smaller rooms, or vice versa.
This costs practically nothing if designed in from the start, but
is impossible to retrofit.
8) Design green.
Example: Design some sort of brise-soleil for the south-facing windows.
Example: The brise-soleil could double as a photovoltaic collector.
Example: In any arid or semi-arid clime, do something useful with
the rainwater that comes off the roof. This is yet another feature
that costs practically nothing if designed in, but is often near-
impossible to retrofit.
Et cetera...............
*) This is not meant to be a complete list. This is meant to be
motivation to read books, consult experts, construct your own
checklists, and double-check everything. There is tremendous
upside if you do things right, and tremendous downside if something
goes wrong.
Possibly constructive suggestion:
https://www.google.com/search?q=%22laboratory+design%22+architect+checklist
I haven't been able to find anything good online. There is stuff
like this:
http://www.ase.org.uk/documents/lab-design-designing-and-planning-laboratories/designing-and-planning-laboratories.pdf
which is better than nothing, but not nearly as detailed as it
should be IMHO. For example, it is wishy-washy about eyewash
stations, and doesn't mention that they should be alarmed. It's
only 60 pages.
You can get hardcopy books with tenfold more detail, including
checklists, which is closer to what's needed.