Re: [Phys-l] it's a dry heat



The cooling of the AC causes the dry air... if the AC is operated properly. When the evaporator section (the cold heat exchanger) is operating at a temperature below the dew point, the household air drawn through the cold exchanger leaves condensed water on the surfaces of the cold exchanger. Depending on air speed, exchanger design, and the incoming room-air temperature, the air leaving the AC unit (inside the house) will be in the neighborhood of 50 F with nearly 100% RH. As that air mixes with the air in the room, the RH of that air goes down because the moisture content is constant but the temperature is rising. If the air leaving the AC is 100% RH at 50 F, and it is entering a room that is maintained at 70 F, then the humidity drops to 50% RH. If the room temperature is maintained at 76 F then the RH drops to about 40% RH.

These are fairly typical numbers for AC operation for fairly normal Midwest USA buildings because the outside RH typically runs higher than 60% and often runs between 80% and 90% RH. In a drier climate the air exiting the AC can be a lower temperature because the heat transfer from the inside cold exchanger to the outside hot exchanger (the compressor unit) is not carrying as much heat of vaporization of the condensed water. If the cold exchanger is not condensing as much water then it can run colder and therefore get the air cooler. However, if the room air is maintained at 75 F and it gets down to 20% RH, the dew point is about 32 F. If the cold exchanger gets that cold (which it can) then the moisture in the air can freeze in the heat exchanger. Ohio is typically humid enough that this rarely happens, but it has happened at my house on warm (but dry) autumn days. Otherwise, with an internal house temperature of 70 to 75 F, and internal RH of 50 to 60%, the air leaving the internal AC exchanger is about 50 F.

A pet peeve I have is HVAC engineers who oversize the AC unit. This means the compressor operates with too low of duty cycle. When the compressor cuts out, the moisture clinging to the cold exchanger surface will evaporate and add humidity back into the room. In addition, since dehumidification is not taking place when the compressor is off, inside sources of moisture (such as respiration and perspiration of people, cooking, bathing, housecleaning) will not be removed. An oversized AC unit that keeps the air at 75 F with only 50% duty cycle can leave the building air between 70% RH and 80% RH and this feels quite "clammy" or "sticky" to me. I prefer the RH around 50%.

Since I have hot-water heat, and therefore no ductwork in my house, I use window AC units. In my two story house I have two 5000 BTU units upstairs and two 5000 BTU units downstairs. They are Energy Star compliant and very quiet. I run one up and one down pretty much continuously. When the outside temperature is below 85-90 F this is all I need. When the outside temperature gets around 88 F or higher, I turn on the other two units. Since I pretty much always have two of the four units running, my household humidity hovers around 50% RH and I find this very comfortable. The only problem I have is some rooms are warmer than others. The humidity is pretty low throughout the house because water vapor diffuses pretty fast due to its low molecular weight.

I am the chair of the Trustees Commission at my church, and last year we installed AC at the church. Rather than one large unit, we installed five units, three cooling the zone with the most people (the sanctuary) and two units cooling the other zones. The units are staged. The first stage in the sanctuary just about runs continuously. If it is not able to maintain the temperature, the second unit comes on. If that can't maintain the temperature, the third unit comes on. When the sanctuary is empty of people, and the outside temperature is not too hot, the second and third stages might not come on at all, but the first stage will run almost continuously. This keeps the humidity below 60% and that is very good for the grand piano, the pipe organ, and other wooden objects (as well as good for people). Had we installed a single large unit that ran with low duty cycle, the humidity would run much higher, and worse, it would fluctuate. If you have a $100,000 pipe organ, you don't want the humidity to fluctuate very much, nor do you want it to get above 80%.

Since we have five separate compressor units (three staged for one zone and two staged for the other zones) we can switch the ordering of the compressor stages. The manufacture suggests we change the ordering either annually or semi-annually so we can spread the work load over all compressors.

This is the first full summer to operate the AC at the church, and because of the unusually hot summer we are giving it a good testing. So far we are pleased. I am also pleased with the operation of my house, and I've been doing that for over 30 years.

Michael D. Edmiston, Ph.D.
Professor of Chemistry and Physics
Chair, Division of Natural and Applied Sciences
Bluffton University
1 University Drive
Bluffton, OH 45817

419.358.3270 (office)
edmiston@bluffton.edu
-----Original Message----- From: Daryl L Taylor
Sent: Tuesday, July 26, 2011 9:26 PM
To: 'Forum for Physics Educators'
Subject: Re: [Phys-l] it's a dry heat

Bob at PC, I'm sure I'm showing my ignorance of AC's, but I thought the biggest benefit of "air conditioners" was the ability to dehumidify the air without the added heat of the mechanism; as in a regular room dehumidifier. This indicates to me that the Nevada "dry heat" simply could not be "dried" any further and you were faced with a limited amount of cooling from the heat "exchange" to the exterior since the sun is so unforgiving out that way.

Or do I have it backwards: the cooling of the AC CAUSES the dry air?

Daryl L Taylor, Fizzix & Astronomy Guy