Chronology Current Month Current Thread Current Date
[Year List] [Month List (current year)] [Date Index] [Thread Index] [Thread Prev] [Thread Next] [Date Prev] [Date Next]

Re: [Phys-l] Watts and VA



On May 9, 2009, at 10:47 PM, Spinozalens@aol.com wrote:

No, a watt isn't a voltamp. Watts are equal to the power factor time the
voltamps. This is because the circuit has capacitance and/ or induction.
Actual power is watts , not voltamps.


P_true= PF*P_app

P_app (apparent power is voltamps)

PF =cos[theta] where theta is the lag or lead in current from voltage due
to the reactance in the circuit.

cos[[theta]= P_true/P_app

Nominal power factors run between . 8 to .9 in most units.


For some loads, measuring electric energy (E=P*t, where P is the average power) is less trivial. Think about energy consumed on a construction site when welding operations are performed. Current fluctuations due to electric arcing are highly irregular. In cases like this, P is measured by digital sampling of V and I, for example, at a frequency randomly modulated, for example, between 1 and 3 MHz. A constant frequency might produce systematic errors, is some situations. Here are two relevant messages from Scott, posted yesterday on a list for cold fusion researchers.

= = = = = = = = = = = = = = = = = = =

Message 1
I would like to point out (again) that the Nyquist criterion does NOT have to be met if your only goal is measurement of the average power in the signal.

The Nyquist criterion (sample at least twice as fast as the highest frequency present) must be met if you wish to construct an accurate picture of the waveform, like an oscilloscope. But such a picture is not necessary when all you want is the average power. For the latter it is sufficient to sample at a much lower frequency and compute a running average of the samples.

It should be noted that lower sampling frequencies permits the designer of a dedicated power analyzer to concentrate more on really important things like the voltage and current measurement accuracy and simultaneity, and the bandwidth/response of the analog front end, which must be able to faithfully track the highest frequencies present in the signal.

Message 2
Andrew wrote: "If you measure I and V at frequencies less than those of the transients/variations, or if you do not measure I and V at "exactly" the same instant you are not including or averaging over any power factors."

You're correct that simultaneity of the V & I measurements is very important but, even if significant power factor is present, it is not necessary for the V & I sample pairs to be taken at high frequency. As long as lots of sample pairs are taken and the sampling frequency is not a sub-harmonic of the signal frequency, the correct result will be obtained when the sample pairs are multiplied together (to get instantaneous power) and averaged (to get average power).

Andrew also wrote: "Have I overlooked anything that could make the real power into the load to be greater than the measured input power? For example, is there anything in the internal operation of an LENR load that could change the measured power factor and alter the measurements to reverse the real < apparent power effect?"

First, with a decent power measurement scheme, any power factor (i.e. phase shift between V and I) will be properly accounted for. So you should not have a real vs apparent power difference. However, as you say, if you were naively multiplying Vrms by Irms to get power, it should always be either correct or an overestimate of the actual power.

I can think of only one problem that could cause actual power to be greater than measured power and that is saturation/overloading of the V or I measurement channels. Most DAQ cards just "peg" their reading when the input exceeds the allowable range....i.e. a voltage of 11 volts applied to a 0-10 volt channel will read 10 volts. But this would be considered an elementary mistake and could be easily avoided by inspecting the V and I signals with an oscilloscope to ensure that they remain within the allowable range at all times.

Scott

= = = = = = = = = = = = = = = = = = =

Ludwik Kowalski, a retired physics teacher and an amateur journalist. Updated links to publications and reviews are at:

http://csam.montclair.edu/~kowalski/cf/ http://csam.montclair.edu/~kowalski/my_opeds.html http://csam.montclair.edu/~kowalski/revcom.html

Also an ESSAY ON ECONOMICS at: http://csam.montclair.edu/~kowalski/economy/essay9.html